hello,

unfortunatly i was unable to locate any sensors for lenovo thinktervers. in particular we would like physical disk smart statuses etc, and general hardware conditions and system health. is there any other way to achieve this?

sincerly

georg franke

lenovo prtg snmp

Created on May 15, 2015 2:46:58 PM



10 Replies

Votes:

0

Hi Georg,

Lenovo just recently aquired the IBM Server line correct? In that case, please take a look at our IBM Server sensors, if SNMP is enabled and the required software is installed, it may work the same way as it would on a IBM server. Please note that required software may have different names since it's now Lenovo's software.

There are our available sensors for IBM Hardware:

SNMP IBM System X Logical Disk Sensor

SNMP IBM System X Physical Disk Sensor

SNMP IBM System X Physical Memory Sensor

SNMP IBM System X System Health Sensor

If you're successful in adding those sensor's, please report back.

Created on May 20, 2015 8:39:48 AM by  Luciano Lingnau [Paessler]



Votes:

0

Hi,

as far as I know they did aquire the System X Productline. Nevertheless the ThinkServer and SystemX are still seperated.

Whereas I'am unable to find any suitable Software for the ThinkServer Productline. SNMP is enabled but as there is no Software providing any SNMP data.

I did also try to install "classic" WMI Sensors for DiskHealth at least which failed as well.

My current guess is that the limitation is mainly on Lenovos side and not PRTG.

If you have any more suggestions I would be very thankful.

Georg

PS: The actual Server I would like to Monitor is an Lenovo ThinkServer RD540

Created on May 26, 2015 8:51:17 AM



Votes:

0

Hello Georg,

I've found some information on the subject, it's compiled below:


Lenovo ThinkServer RD240 Software User's Manual / Page 237

6.6.2.3 ThinkServer SAS SNMP MIB Location
After you install the ThinkServer SAS SNMP Agent package, the MIB file ThinkServer-AdapterSAS.mib is installed under /etc/ThinkServer_mrdsnmp/sas directory.


ThinkServer RAID Management Tools

Please see the following link from Lenovo's documentation, for management of servers that use a LSI RAID Controller.


If that documentation is accurate, it is possible to import the MIB using our SNMP Importer Tool and then adding a SNMP Library Sensor.
You may also need to create/customize a Lookup file to see the correct Ok/Warning/Down status when something fails.

Unfortunately that only regards the RAID Controler/disks, I wasn't able to find any documentation that states that the above mentioned hardware has a proper MIB to monitor the hardware's status.

Created on May 26, 2015 11:18:49 AM by  Luciano Lingnau [Paessler]



Votes:

0

Hi, By now (01.2017) IBM has retired their "System Director Platform" needed to connect PRTG's IBM sensors. I really need to monitor my brand new Lenovo Server, specially its HDDs.

Lenovo offers dedicated MIB files, but the PRTG MIB tool fails to import them:

http://support.lenovo.com/il/en/downloads/ds102403

Any idea?

Thanks, Ariel.

Created on Jan 8, 2017 1:47:38 PM



Votes:

0

Hello Ariel, thank you for your input.

The issue with the linked files is that they don't follow the SNMP/MIB syntax, that's also why the MIB Importer fails to import it. I did however address the most grotesque issues and created an importable/usable MIB File. It's the Text in the box below, just create a new text (.txt) file copy this text into it and save it as ThinkServer-TSM.mib:

Note: Provided as-is without any warranties. Alternatively, contact the vendor and ask them to correct the MIB Instead. This should be importable and usable with PRTG now.

---------------------------------------------------------------------------
--
-- Title: Systems Management Instrumentation MIB of Lenovo ThinkServer
--
-- Version: 1.0.0
--
-- Release Date: 2014.11.11
--
-- Description: This MIB defines MIB objects that make system instrumentation
-- data available to SNMP management applications.
--
-- Copyright (c) 2013-2014 Lenovo Corp.
-- All Rights Reserved.
--
--
-- OID Format Legend:
--   <a> = attribute ID
--   <i> = index ID
--
---------------------------------------------------------------------------

---------------------------------------------------------------------------
-- Begin MIB
---------------------------------------------------------------------------

ThinkServer-TSM DEFINITIONS ::= BEGIN
IMPORTS
    MODULE-IDENTITY,
    OBJECT-IDENTITY,
    OBJECT-TYPE,
    Integer32,
    Integer32, Opaque, enterprises
        FROM SNMPv2-SMI
    TEXTUAL-CONVENTION, DisplayString
        FROM SNMPv2-TC;


---------------------------------------------------------------------------
-- Object Identifiers
--------------------------------------------------------------------------

thinkServerMIB MODULE-IDENTITY
    LAST-UPDATED "201701090914Z"
    ORGANIZATION "Lenovo Group"
    CONTACT-INFO "[email protected]"
    DESCRIPTION  
        "EPG-ThinkServer"

    REVISION     "201701090914Z"
    DESCRIPTION  
        "Fixed upperxlowercase and minor issues (LucianoLingnau @ Paessler AG)"

        
    REVISION     "201411110000Z"
    DESCRIPTION  
        "first release"

::= { enterprises 19046 }

platformObjects OBJECT IDENTIFIER ::= { thinkServerMIB 10 }
---bmcObjects OBJECT IDENTIFIER ::= { thinkServerMIB 3 }
---chassisInfoObjects OBJECT IDENTIFIER ::= { thinkServerMIB 4}
---boardInfoObjects OBJECT IDENTIFIER ::= { thinkServerMIB 5}
---productInfoObjects OBJECT IDENTIFIER ::= { thinkServerMIB 6}

---------------------------------------------------------------------------
-- "Float32TC" was used originally(but not importer). Replaced with "Float" and added the tc below.
--------------------------------------------------------------------------

Float ::= TEXTUAL-CONVENTION
    STATUS      current
    DESCRIPTION
        ""
    SYNTAX Opaque (SIZE (7))
    
---------------------------------------------------------------------------
-- platformName
--------------------------------------------------------------------------
platformName OBJECT-TYPE
    SYNTAX      DisplayString
    MAX-ACCESS  read-only
    STATUS      current
    DESCRIPTION "The server name"
    ::= { thinkServerMIB 1 }

---------------------------------------------------------------------------
-- systemLocation
--------------------------------------------------------------------------
systemLocation OBJECT-TYPE
    SYNTAX      DisplayString
    MAX-ACCESS  read-only
    STATUS      current
    DESCRIPTION "The System Location"
    ::= { thinkServerMIB 2 }


---------------------------------------------------------------------------
-- sensorTable 
---------------------------------------------------------------------------	
sensorTable OBJECT-TYPE
    SYNTAX      SEQUENCE OF SensorEntry
    MAX-ACCESS  not-accessible
    STATUS      current
    DESCRIPTION
        "A table of sensor entries."
    ::= { platformObjects 2 }

---------------------------------------------------------------------------
-- sensorEntry 
---------------------------------------------------------------------------	
sensorEntry OBJECT-TYPE
    SYNTAX        SensorEntry
    MAX-ACCESS    not-accessible
    STATUS        current
    DESCRIPTION
        "An entry in the sensor table."
    INDEX        { sensorIndex }
    ::= { sensorTable 1 }

SensorEntry ::=
    SEQUENCE {
        sensorIndex      Integer32,
        sensorName       DisplayString,
        sensorNumber     Integer32,
        sensorValue      INTEGER
    }

sensorIndex OBJECT-TYPE
    SYNTAX        Integer32 (1..65535)
    MAX-ACCESS  not-accessible
    STATUS        current
    DESCRIPTION
        "The unique value which identifies the sensor."
    ::= { sensorEntry 1 }


sensorName OBJECT-TYPE
    SYNTAX        DisplayString
    MAX-ACCESS  read-only
    STATUS        current
    DESCRIPTION
        "A textual full name assigned to a sensor."
    ::= { sensorEntry 2 }	
	
sensorNumber OBJECT-TYPE
    SYNTAX        Integer32 (1..65535)
    MAX-ACCESS  read-only
    STATUS        current
    DESCRIPTION
        "The sensor number."
    ::= { sensorEntry 3 }	
	
sensorValue OBJECT-TYPE
    SYNTAX        INTEGER
    MAX-ACCESS  read-only
    STATUS        current
    DESCRIPTION
        "The sensor value."
    ::= { sensorEntry 4 }	

---------------------------------------------------------------------------
-- fRUTables 
---------------------------------------------------------------------------	
fRUTable OBJECT-TYPE
    SYNTAX      SEQUENCE OF FRUEntry
    MAX-ACCESS  not-accessible
    STATUS      current
    DESCRIPTION
        "A table of platform FRU entries."
    ::= { platformObjects 3 }

---------------------------------------------------------------------------
-- fRUEntry (FRU)
---------------------------------------------------------------------------	
fRUEntry OBJECT-TYPE
    SYNTAX        FRUEntry
    MAX-ACCESS    not-accessible
    STATUS        current
    DESCRIPTION
        "An entry in the FRU table."
    INDEX        { fRUIndex }
    ::= { fRUTable 1 }

FRUEntry ::=
    SEQUENCE {
        fRUIndex      Integer32,
        fRUVendorName      Integer32,
        fRUVendorPartNumber      Integer32,
        fRUVendorAssemblyRevision      Integer32,
        fRUVendorSerialNumber      Integer32
    }
    
fRUIndex OBJECT-TYPE
    SYNTAX        Integer32 (1..65535)
    MAX-ACCESS  not-accessible
    STATUS        current
    DESCRIPTION
        "The unique value which identifies the FRU."
    ::= { fRUEntry 1 }

fRUVendorName OBJECT-TYPE
    SYNTAX        Integer32 (1..65535)
    MAX-ACCESS  read-only
    STATUS        current
    DESCRIPTION
        "The vendor name for the FRU."
    ::= { fRUEntry 2 }	
	
fRUVendorPartNumber OBJECT-TYPE
    SYNTAX        Integer32 (1..65535)
    MAX-ACCESS  read-only
    STATUS        current
    DESCRIPTION
        "The vendor part number for the FRU."
    ::= { fRUEntry 3 }	

fRUVendorAssemblyRevision OBJECT-TYPE
    SYNTAX        Integer32 (1..65535)
    MAX-ACCESS  read-only
    STATUS        current
    DESCRIPTION
        "The vendor assembley revision for the FRU."
    ::= { fRUEntry 4 }	
	
fRUVendorSerialNumber OBJECT-TYPE
    SYNTAX        Integer32 (1..65535)
    MAX-ACCESS  read-only
    STATUS        current
    DESCRIPTION
        "The vendor serial number for the FRU."
    ::= { fRUEntry 5 }	
    
    
END

If it fails to find any compatible data in PRTG (when deploying the SNMP Library sensor), please perform a walk from the following OID with our SNMP Tester and share the results:

1.3.6.1.4.1.19046.10

If you need a guide to import the MIB, please refer to:

One deal-breaker with this MIB file, is that there's no "syntax definition" for the sensorValue, this may make getting alerts tricky, you'll have to set-up limits to get the sensors alerting.

Best Regards,
Luciano Lingnau [Paessler Support]

Created on Jan 9, 2017 8:23:29 AM by  Luciano Lingnau [Paessler]

Last change on Jan 9, 2017 8:29:32 AM by  Luciano Lingnau [Paessler]



Votes:

0

Hi Luciano and thanks for your help.

I've successfully imported the customized MIB file into prtg.

When adding the corresponding snmp library sensor I get "No available interfaces on this device (code: PE049)" error.

snmp tester walk with 1.3.6.1.4.1.19046.10 OID log:

----------------------- New Test -----------------------
Paessler SNMP Tester 5.2.3 Computername: SYSMON Interface: 172.20.0.252
10/01/2017 09:55:29 (1 ms) : Device: 172.20.0.18
10/01/2017 09:55:29 (2 ms) : SNMP V2c
10/01/2017 09:55:29 (3 ms) : Walk 1.3.6.1.4.1.19046.10
----------------------- New Test -----------------------
Paessler SNMP Tester 5.2.3 Computername: SYSMON Interface: 172.20.0.252
10/01/2017 09:56:33 (3 ms) : Device: 172.20.0.18
10/01/2017 09:56:33 (4 ms) : SNMP V1
10/01/2017 09:56:33 (5 ms) : Walk 1.3.6.1.4.1.19046.10
10/01/2017 09:56:33 (8 ms) : Error: 2

Regards, Ariel

Created on Jan 10, 2017 8:00:29 AM

Last change on Jan 10, 2017 8:43:06 AM by  Luciano Lingnau [Paessler]



Votes:

0

Hello Ariel,
thank you for your reply and tests.

That's not good I'm afraid. The lack of a reply (or the error 2) basically tells us that this system don't know the polled/walked OID. Have you confirmed that SNMP is enabled on 172.20.0.18?

You can confirm this by doing a walk of 1.3.6.1.2.1.1 or 1.3.6. If you get valid replies to this query, contact Lenovo/IBM and inquiry about why the server isn't responding to queries from the OID that are part of the appropriate MIB.

Best Regards,
Luciano Lingnau [Paessler Support]

Created on Jan 10, 2017 8:54:21 AM by  Luciano Lingnau [Paessler]



Votes:

0

Hi Luciano,

The server has SNMP enabled and working, so I'll try to get some help from LENOVO.

I really appreciate your concern.

Ariel.

Created on Jan 10, 2017 12:19:57 PM



Votes:

0

Hello,

Sorry for updating a "4 months ago" post, but we had a disk failure on our ThinkServer RD440 and it took a few days before we realized it. We have PRTG installed in intern of our business and on our remote cloud. We're very happy with it but can't apparently correctly monitor our Lenovo Thinkserver.

While Googling, I found this post and I would like to know if any of you have an update about this? It's really annoying and I know it's PRTG's fault but if someone found a solution for this, it would be very helpful.

(I already tried to SNMPWalk with the given OIDs and I can't find them...)

Created on Apr 20, 2017 12:09:03 PM



Votes:

0

Hello Nolwyn,
thank you for your reply and no worries about updating the 4 months old post.

I had one more look for this subject. This is what I located:

1. First, I began with the system's Datasheet, which claims:

One of the most important features of the RD440 — and all ThinkServer systems — is that it uses open industry standards and protocols so it integrates easily into your multi-vendor environment. That means you can use your existing management tools with the RD440 or try ours at no additional charge. In addition to a front-side diagnostic panel, the RD440 offers a suite of intuitive ThinkServer lifecycle tools that make management easy so you can focus on IT projects that drive your business. These tools include configuration, firmware, and rack power optimizers, as well as a way to conveniently searchfor, monitor, and manage your servers.

Which means that there must be a way to monitor these.
2. I've then looked further and stumbled uppon the ThinkServer EasyManage tool. Which is of course proprietary.

3. After a bit more search I've located this document:

If the information from the document above is "True", it's actually quite interesting. There's a table:

CapabilityThinkServer Management ModuleThinkServer System Manager
Supported Systems3rd and 4th generation ThinkServer Except TS130, TS140, RS1405th generation ThinkServer
Supported StandardsIPMI version 2.0, DCMI 1.0 (2P racks only),SMASH-CLI (limited), WS-MAN (limited)IPMI version 2.0, DCMI 1.0, SMASH-CLI, WS-MAN SNMP v3 (Gets)
Embedded Command Line InterfaceSMASH-CLI (limited)SMASH-CLI, PowerShell

If this is correct (and applies), this is good news for owners of 5th generation ThinkServer servers. This all appears to apply only to the out-of-band interface, but the following should work with PRTG:

  • IPMI (Limited)
  • SNMP v3 (Gets)
  • PowerShell

Without access to any MIB, Powershell may be the best option. The document mentions the following Powershell cmdlet (which must be imported via some software package):

Invoke-TMMCLI [-CommandName]
<COMMAND_NAME>
[COMMAND_PARAMETERS] [-CommandArgs]
@ {[COMMAND_ARGUMENTS]}

My general advise is: Contact Lenovo/IBM, the features mentioned in this document look very promissing, if all that is true it would offer a lot of flexibility for monitoring with PRTG.

And if you're a PRTG user and got any of this working on your IBM hardware, share your thoughts/comments, they are very welcome.

Best Regards,
Luciano Lingnau [Paessler Support]

Created on Apr 20, 2017 12:56:12 PM by  Luciano Lingnau [Paessler]




Disclaimer: The information in the Paessler Knowledge Base comes without warranty of any kind. Use at your own risk. Before applying any instructions please exercise proper system administrator housekeeping. You must make sure that a proper backup of all your data is available.