Since updating to the current Dell iDRAC firmware I cannot get the PRTG ipmi sensor to connect. My other tools that access IPMI on the servers are still working so I am guessing this is a compatibility issue with the utility used by prtg. I am guessing this directly relates to dell removing ipmi 1.5 and only supporting 2.0 in its current firmware's. is this a known issue?
Best Answer
I found the fix for this issue.
Just add "-F lan2" to the user name. E.g.:
root -F lan2 |
Created on Dec 18, 2015 2:48:22 PM by
droorda
(100)
●1
●1
Last change on Dec 18, 2015 3:19:18 PM by
Luciano Lingnau [Paessler Support]
9 Replies
This is something that we can try and test here. I'll let you know what we find out.
I was able to test this here with a Dell Server running version 1.97 Firmware and IMPI 2.0 and was able to read Fan Speed, Temperature, Voltage and the Power Supply status so it's definitely not a bug with the sensor. When creating the sensor have you made sure that all of the requirements are met and that the credentials entered are correct? Have you also tried re-creating the sensor? If all of this is failing, can you please tell us specifically what error you get when creating the sensor?
I went ahead and tested with the tool you use to gather the data ipmiutil ver 2.91 isensor: version 2.91 Opening lan connection to node ServerName Connecting to node 192.168.11.11 ipmilan_open_session error, rv = -3 ipmilan receive from BMC failed ipmi_open error = -3 ipmiutil sensor, receive from BMC failed
I also tested with the correct version of the tool 2.96 and I get the same results. I have verified this behavior across several properly configured servers. I can successfully connect to each of these systems with the dell ipmi tool so I know they are setup correctly. I can also confirm this is an issue with the latest firmware for the drac 7 & 8 cards. I assume it is because of Dell removing compatibility with ipmi 1.5 https://www.kb.cert.org/vuls/id/BLUU-9RDQHM "therefore support for the IPMI 1.5 version of the protocol has been permanently removed" This appears to be a violation of the IPMIv2.0 standard, which I assume is what is causing the tool to stop working. Is there a chance that you will update the tool to handle this or am I stuck waiting for someone to update the project?
I was able to verify this as well and will talk with the developer about what we can do on our end. I will post here as soon as I know more.
At the moment, there aren't enough people with this issue to justify us completely re-writing the sensor. If we see more people with this issue then we will consider changing the sensor to use another utility or re-write the existing one.
I found the fix for this issue.
Just add "-F lan2" to the user name. E.g.:
root -F lan2 |
Created on Dec 18, 2015 2:48:22 PM by
droorda
(100)
●1
●1
Last change on Dec 18, 2015 3:19:18 PM by
Luciano Lingnau [Paessler Support]
Thanks for adding this to the KB droorda! I've tested this out in our environment and it works for us as well. Apparently this forces the ipmiutil to load the lan2 driver thereby forcing it to only use impi v.2. More can be read about the switches in the man page for the utility.
oh WOW! this also helped me too w prtg v18 and a supermicro system, prtg was working fine until i changed the sm's ipmi admin account to a non default password (ie until i secured it). i kept getting wrong password from prtg.
add this made it work!! so in my case i input into prtg (when it asks for the IPMI creds):
ADMIN root -F lan2 |
(then my secure password)
and it finally works!! thank you so much for coming back here and updating the answer! (i had emailed prtg support also)
Created on Sep 25, 2018 5:12:10 AM by
JimLovePRTG
(41)
●2
Last change on Sep 28, 2018 6:59:06 AM by
JimLovePRTG
(41)
●2
I would like to correct that for supermicro, you don't need "root", username is only
ADMIN -F lan2
Without this flag i had this error:
...
GetSessChallenge: Invalid data field in request