Hi, i want to monitor temperature of cisco asr9010 router. snmpwalk return value but PRTG unable to retrieve temperature data from the device.
OID : 1.3.6.1.2.1.47.1.1.1.1.7 OID : 1.3.6.1.4.1.9.9.91.1.1.1.1.4
Votes:
Hi, i want to monitor temperature of cisco asr9010 router. snmpwalk return value but PRTG unable to retrieve temperature data from the device.
OID : 1.3.6.1.2.1.47.1.1.1.1.7 OID : 1.3.6.1.4.1.9.9.91.1.1.1.1.4
asr9010 cisco-router snmpwalk temperature
Created on May 5, 2016 8:22:06 AM
Last change on May 5, 2016 10:40:12 AM by
Luciano Lingnau [Paessler]
5 Replies
Votes:
Hello,
we appreciate your contact.
Have you considered using the built-in SNMP Cisco System Health Sensor which monitors among other things the temperature.
Regarding the OID's that you've posted:
This is entPhysicalName:
The textual name of the physical entity. The value of this object should be the name of the component as assigned by the local device and should be suitable for use in commands entered at the device's `console'. This might be a text name (e.g., `console') or a simple component number (e.g., port or module number, such as `1'), depending on the physical component naming syntax of the device. If there is no local name, or if this object is otherwise not applicable, then this object contains a zero-length string. Note that the value of entPhysicalName for two physical entities will be the same in the event that the console interface does not distinguish between them, e.g., slot-1 and the card in slot-1. |
You won't be able to measure the temperature from this OID.
This is entSensorValue:
This variable reports the most recent measurement seen by the sensor. To correctly display or interpret this variable's value, you must also know entSensorType, entSensorScale, and entSensorPrecision. However, you can compare entSensorValue with the threshold values given in entSensorThresholdTable without any semantic knowledge. |
Please perform a walk using our SNMP Tester first to identify all available indexes and then copy the OID's for the desired values into an SNMP Custom Sensor in PRTG.
Best Regards,
Votes:
i have tried using the default build-in health sensor but it didnt return any value.
Votes:
Hello,
thank you for your reply.
And did the custom sensors on these OID's or the SNMP Walk on "1.3.6.1.4.1.9.9.91.1.1.1.1.4" using our SNMP Tester Succeed? If not it could be that SNMP is not enabled/configured on the ASR9010 or the device doesn't offer such readings via SNMP.
Best Regards,
Votes:
Hi, we tested using snmpwalk and is working. Only the PRTG cannot retrieve temperature value.
----------------------- New Test ----------------------- Paessler SNMP Tester 5.1.3 28/04/2016 18:22:06 (23 ms) : Device: x.x.x.x 28/04/2016 18:22:06 (33 ms) : SNMP V2c 28/04/2016 18:22:06 (46 ms) : Walk 1.3.6.1.4.1.9.9.91.1.1.1.1.4 28/04/2016 18:22:06 (70 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.67605 = "53" 28/04/2016 18:22:06 (93 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.138542 = "328" 28/04/2016 18:22:06 (117 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.320862 = "1814" 28/04/2016 18:22:06 (143 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.322450 = "1201" 28/04/2016 18:22:06 (165 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.727162 = "0" 28/04/2016 18:22:06 (186 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.2404345 = "464" 28/04/2016 18:22:06 (262 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.3355929 = "54515" 28/04/2016 18:22:06 (287 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.4010525 = "280" 28/04/2016 18:22:06 (309 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.4306232 = "-32768" 28/04/2016 18:22:06 (331 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.4436046 = "212" 28/04/2016 18:22:06 (356 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.4437634 = "3330" 28/04/2016 18:22:06 (378 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.4761191 = "1496" 28/04/2016 18:22:06 (401 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.4762811 = "1218" 28/04/2016 18:22:06 (422 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.5329584 = "26" 28/04/2016 18:22:06 (442 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.5574832 = "1799" 28/04/2016 18:22:06 (462 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.5645168 = "277" 28/04/2016 18:22:06 (484 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.5773465 = "1000" 28/04/2016 18:22:06 (507 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.5775149 = "749" 28/04/2016 18:22:06 (531 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.5778357 = "1100" 28/04/2016 18:22:06 (552 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.5789569 = "309" 28/04/2016 18:22:06 (576 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.5909380 = "1800" 28/04/2016 18:22:06 (600 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.5922230 = "748" 28/04/2016 18:22:06 (625 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.5925406 = "1200" 28/04/2016 18:22:06 (645 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.5926994 = "5000" 28/04/2016 18:22:06 (669 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.6106457 = "1199" 28/04/2016 18:22:06 (692 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.6109729 = "1199" 28/04/2016 18:22:06 (714 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.6111349 = "7000" 28/04/2016 18:22:06 (735 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.6256778 = "1199" 28/04/2016 18:22:06 (758 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.6258398 = "1499" 28/04/2016 18:22:06 (778 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.6259986 = "744" 28/04/2016 18:22:06 (804 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.6673654 = "3298" 28/04/2016 18:22:06 (825 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.6676830 = "1099" 28/04/2016 18:22:06 (848 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.6678418 = "1800" 28/04/2016 18:22:06 (872 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.6869781 = "7050" 28/04/2016 18:22:06 (893 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.6888699 = "-32768" 28/04/2016 18:22:06 (918 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.7227062 = "1500" 28/04/2016 18:22:06 (938 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.7228618 = "1200" 28/04/2016 18:22:06 (959 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.7526020 = "1199" 28/04/2016 18:22:07 (982 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.7641118 = "3324" 28/04/2016 18:22:07 (1003 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.7642706 = "281" 28/04/2016 18:22:07 (1026 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.7645119 = "358" 28/04/2016 18:22:07 (1048 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.7646707 = "3284" 28/04/2016 18:22:07 (1071 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.7648263 = "1193" 28/04/2016 18:22:07 (1095 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.7726369 = "1099" 28/04/2016 18:22:07 (1119 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.7727989 = "1000" 28/04/2016 18:22:07 (1143 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.7931360 = "606" 28/04/2016 18:22:07 (1165 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.8895994 = "25" 28/04/2016 18:22:07 (1189 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.10735504 = "2504" 28/04/2016 18:22:07 (1210 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.10737188 = "10598" 28/04/2016 18:22:07 (1233 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.10738808 = "388" 28/04/2016 18:22:07 (1253 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.10743073 = "3300" 28/04/2016 18:22:07 (1277 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.10744693 = "1050" 28/04/2016 18:22:07 (1298 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.10845139 = "306" 28/04/2016 18:22:07 (1321 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.10889081 = "1506" 28/04/2016 18:22:07 (1344 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.10890637 = "1055" 28/04/2016 18:22:07 (1369 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.10892225 = "1000" 28/04/2016 18:22:07 (1390 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.11029231 = "3299" 28/04/2016 18:22:07 (1417 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.11037718 = "1004" 28/04/2016 18:22:07 (1438 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.11039402 = "1190" 28/04/2016 18:22:07 (1460 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.11042610 = "1104" 28/04/2016 18:22:07 (1482 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.11196778 = "1" 28/04/2016 18:22:07 (1505 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.11229452 = "1199" 28/04/2016 18:22:07 (1526 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.11231040 = "749" 28/04/2016 18:22:07 (1549 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.11234344 = "1099" 28/04/2016 18:22:07 (1572 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.11239623 = "1808" 28/04/2016 18:22:07 (1593 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.11741636 = "436" 28/04/2016 18:22:07 (1618 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.11741762 = "7020" 28/04/2016 18:22:07 (1638 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.12536348 = "280" 28/04/2016 18:22:07 (1660 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.12597551 = "1499" 28/04/2016 18:22:07 (1684 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.12599139 = "490" 28/04/2016 18:22:07 (1708 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.12602315 = "1000" 28/04/2016 18:22:07 (1729 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.12670880 = "3300" 28/04/2016 18:22:07 (1751 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.12672500 = "1800" 28/04/2016 18:22:07 (1774 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.12674056 = "1099" 28/04/2016 18:22:07 (1799 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.12905956 = "751" 28/04/2016 18:22:07 (1822 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.12907576 = "5007" 28/04/2016 18:22:07 (1847 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.13102294 = "551" 28/04/2016 18:22:07 (1868 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.13443524 = "7050" 28/04/2016 18:22:07 (1893 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.13584276 = "1000" 28/04/2016 18:22:07 (1918 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.13585960 = "1500" 28/04/2016 18:22:07 (1941 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.13805629 = "7050" 28/04/2016 18:22:07 (1961 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.14020599 = "3350" 28/04/2016 18:22:08 (1986 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.14022155 = "225" 28/04/2016 18:22:08 (2006 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.14263962 = "26" 28/04/2016 18:22:08 (2029 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.14421321 = "289" 28/04/2016 18:22:08 (2050 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.15177601 = "7050" 28/04/2016 18:22:08 (2074 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.15494752 = "0" 28/04/2016 18:22:08 (2095 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.15516807 = "0" 28/04/2016 18:22:08 (2118 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.15858003 = "2100" 28/04/2016 18:22:08 (2140 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.15986678 = "1202" 28/04/2016 18:22:08 (2164 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.15988234 = "1804" 28/04/2016 18:22:08 (2186 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.16845282 = "1100" 28/04/2016 18:22:08 (2208 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.17096855 = "1501" 28/04/2016 18:22:08 (2231 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.17098539 = "1199" 28/04/2016 18:22:08 (2254 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.17503155 = "0" 28/04/2016 18:22:08 (2279 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.17977066 = "7020" 28/04/2016 18:22:08 (2305 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.19181894 = "305" 28/04/2016 18:22:08 (2331 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.20133606 = "2100" 28/04/2016 18:22:08 (2358 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.20788202 = "433" 28/04/2016 18:22:08 (2383 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.21082225 = "-32768" 28/04/2016 18:22:08 (2408 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.21083781 = "-32768" 28/04/2016 18:22:08 (2430 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.21212039 = "0" 28/04/2016 18:22:08 (2454 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.21538804 = "3319" 28/04/2016 18:22:08 (2477 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.21540360 = "1824" 28/04/2016 18:22:08 (2501 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.22107165 = "315" 28/04/2016 18:22:08 (2522 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.22352413 = "3299" 28/04/2016 18:22:08 (2550 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.22422749 = "0" 28/04/2016 18:22:08 (2575 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.22551142 = "1200" 28/04/2016 18:22:08 (2596 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.22552762 = "748" 28/04/2016 18:22:08 (2621 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.22555906 = "1099" 28/04/2016 18:22:08 (2645 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.22567278 = "476" 28/04/2016 18:22:08 (2668 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.22686993 = "1199" 28/04/2016 18:22:08 (2694 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.22701399 = "1050" 28/04/2016 18:22:08 (2717 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.22703083 = "3300" 28/04/2016 18:22:08 (2794 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.22831118 = "10600" 28/04/2016 18:22:08 (2820 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.22884134 = "1000" 28/04/2016 18:22:08 (2844 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.22887310 = "1000" 28/04/2016 18:22:08 (2867 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.22888898 = "1100" 28/04/2016 18:22:08 (2892 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.23034391 = "1799" 28/04/2016 18:22:08 (2917 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.23036075 = "743" 28/04/2016 18:22:08 (2940 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.23403447 = "7080" 28/04/2016 18:22:08 (2965 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.23452823 = "748" 28/04/2016 18:22:09 (2986 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.23454507 = "1199" 28/04/2016 18:22:09 (3014 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.23666248 = "-32768" 28/04/2016 18:22:09 (3038 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.24003023 = "2499" 28/04/2016 18:22:09 (3063 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.24004611 = "749" 28/04/2016 18:22:09 (3087 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.24007915 = "1100" 28/04/2016 18:22:09 (3114 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.24303633 = "1199" 28/04/2016 18:22:09 (3138 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.24305317 = "5002" 28/04/2016 18:22:09 (3163 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.24418795 = "0" 28/04/2016 18:22:09 (3186 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.24422668 = "418" 28/04/2016 18:22:09 (3208 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.24424256 = "3307" 28/04/2016 18:22:09 (3229 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.24425876 = "1825" 28/04/2016 18:22:09 (3252 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.24503950 = "5000" 28/04/2016 18:22:09 (3275 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.24505538 = "1000" 28/04/2016 18:22:09 (3297 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.24708941 = "454" 28/04/2016 18:22:09 (3319 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.25671987 = "255" 28/04/2016 18:22:09 (3342 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.27514801 = "5004" 28/04/2016 18:22:09 (3365 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.27516357 = "750" 28/04/2016 18:22:09 (3388 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.27520654 = "10859" 28/04/2016 18:22:09 (3408 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.27522242 = "1100" 28/04/2016 18:22:09 (3430 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.27622816 = "438" 28/04/2016 18:22:09 (3451 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.27666630 = "1504" 28/04/2016 18:22:09 (3472 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.27668250 = "2516" 28/04/2016 18:22:09 (3493 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.27669934 = "1104" 28/04/2016 18:22:09 (3516 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.27806844 = "1787" 28/04/2016 18:22:09 (3538 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.27813807 = "1000" 28/04/2016 18:22:09 (3562 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.27815395 = "994" 28/04/2016 18:22:09 (3583 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.27972771 = "0" 28/04/2016 18:22:09 (3607 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.28007065 = "1799" 28/04/2016 18:22:09 (3629 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.28008749 = "746" 28/04/2016 18:22:09 (3652 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.28017236 = "3279" 28/04/2016 18:22:09 (3674 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.28519249 = "415" 28/04/2016 18:22:09 (3695 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.28612240 = "7020" 28/04/2016 18:22:09 (3720 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.29314025 = "178" 28/04/2016 18:22:09 (3741 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.29375164 = "3299" 28/04/2016 18:22:09 (3769 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.29376752 = "303" 28/04/2016 18:22:09 (3790 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.29379928 = "2500" 28/04/2016 18:22:09 (3814 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.29450049 = "1199" 28/04/2016 18:22:09 (3840 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.29451669 = "748" 28/04/2016 18:22:09 (3862 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.29680361 = "2510" 28/04/2016 18:22:09 (3885 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.29683569 = "393" 28/04/2016 18:22:09 (3907 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.29685125 = "11026" 28/04/2016 18:22:09 (3929 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.29784763 = "328" 28/04/2016 18:22:09 (3954 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.29878383 = "557" 28/04/2016 18:22:10 (3974 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.30360365 = "1000" 28/04/2016 18:22:10 (4000 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.30361953 = "1500" 28/04/2016 18:22:10 (4021 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.30363573 = "438" 28/04/2016 18:22:10 (4044 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.30799768 = "0" 28/04/2016 18:22:10 (4066 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.31039955 = "322" 28/04/2016 18:22:10 (4090 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.31198934 = "504" 28/04/2016 18:22:10 (4113 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.32270777 = "3350" 28/04/2016 18:22:10 (4137 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.32272333 = "219" 28/04/2016 18:22:10 (4158 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.32294420 = "0" 28/04/2016 18:22:10 (4233 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.32635680 = "54210" 28/04/2016 18:22:10 (4256 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.32762639 = "1897" 28/04/2016 18:22:10 (4281 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.32764227 = "1044" 28/04/2016 18:22:10 (4305 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.33621307 = "507" 28/04/2016 18:22:10 (4329 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.33874532 = "1883" 28/04/2016 18:22:10 (4353 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.33876152 = "1047" 28/04/2016 18:22:10 (4378 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.34279116 = "3339" 28/04/2016 18:22:10 (4401 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.34280704 = "257" 28/04/2016 18:22:10 (4426 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.35957919 = "48" 28/04/2016 18:22:10 (4448 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.37564195 = "503" 28/04/2016 18:22:10 (4472 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.37861394 = "-32768" 28/04/2016 18:22:10 (4501 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.37989652 = "1" 28/04/2016 18:22:10 (4525 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.38317973 = "5006" 28/04/2016 18:22:10 (4550 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.38884842 = "485" 28/04/2016 18:22:10 (4579 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.39130090 = "1785" 28/04/2016 18:22:10 (4603 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.39200426 = "0" 28/04/2016 18:22:10 (4625 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.39327167 = "1799" 28/04/2016 18:22:10 (4650 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.39328755 = "747" 28/04/2016 18:22:10 (4673 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.39343271 = "1202" 28/04/2016 18:22:10 (4699 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.39464702 = "1200" 28/04/2016 18:22:10 (4722 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.39479076 = "1099" 28/04/2016 18:22:10 (4749 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.39480696 = "10625" 28/04/2016 18:22:10 (4824 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.39607111 = "54167" 28/04/2016 18:22:10 (4848 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.39663303 = "999" 28/04/2016 18:22:10 (4875 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.39664923 = "1100" 28/04/2016 18:22:10 (4900 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.39812068 = "1499" 28/04/2016 18:22:10 (4924 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.39813688 = "1199" 28/04/2016 18:22:10 (4949 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.40230500 = "1000" 28/04/2016 18:22:11 (4974 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.40232120 = "1799" 28/04/2016 18:22:11 (4998 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.40442241 = "-32768" 28/04/2016 18:22:11 (5023 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.40443861 = "-32768" 28/04/2016 18:22:11 (5047 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.40780636 = "1499" 28/04/2016 18:22:11 (5073 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.40782224 = "745" 28/04/2016 18:22:11 (5094 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.40785528 = "1199" 28/04/2016 18:22:11 (5122 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.41081342 = "1800" 28/04/2016 18:22:11 (5144 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.41196408 = "0" 28/04/2016 18:22:11 (5170 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.41200281 = "11119" 28/04/2016 18:22:11 (5196 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.41201965 = "888" 28/04/2016 18:22:11 (5223 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.41278387 = "1199" 28/04/2016 18:22:11 (5244 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.41279943 = "7000" 28/04/2016 18:22:11 (5266 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.41281563 = "1199" 28/04/2016 18:22:11 (5288 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.41486554 = "301" 28/04/2016 18:22:11 (5312 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.42449536 = "461" 28/04/2016 18:22:11 (5337 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.44292382 = "3282" 28/04/2016 18:22:11 (5360 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.44293970 = "903" 28/04/2016 18:22:11 (5382 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.44295091 = "891" 28/04/2016 18:22:11 (5408 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.44296647 = "1100" 28/04/2016 18:22:11 (5431 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.44298267 = "1000" 28/04/2016 18:22:11 (5453 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.44400397 = "481" 28/04/2016 18:22:11 (5474 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.44442655 = "1813" 28/04/2016 18:22:11 (5497 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.44444243 = "754" 28/04/2016 18:22:11 (5518 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.44584393 = "7000" 28/04/2016 18:22:11 (5543 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.44591420 = "1509" 28/04/2016 18:22:11 (5564 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.44593008 = "1037" 28/04/2016 18:22:11 (5587 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.44750384 = "0" 28/04/2016 18:22:11 (5610 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.44784742 = "1499" 28/04/2016 18:22:11 (5635 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.44786362 = "747" 28/04/2016 18:22:11 (5658 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.44949055 = "7080" 28/04/2016 18:22:11 (5681 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.45296958 = "34" 28/04/2016 18:22:11 (5705 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.46091638 = "5" 28/04/2016 18:22:11 (5728 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.46152713 = "1799" 28/04/2016 18:22:11 (5748 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.46154333 = "1800" 28/04/2016 18:22:11 (5771 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.46227758 = "1799" 28/04/2016 18:22:11 (5792 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.46229346 = "1000" 28/04/2016 18:22:11 (5815 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.46457974 = "3305" 28/04/2016 18:22:11 (5840 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.46461150 = "272" 28/04/2016 18:22:11 (5864 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.46462738 = "906" 28/04/2016 18:22:11 (5887 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.46562312 = "290" 28/04/2016 18:22:11 (5909 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.46655996 = "50" 28/04/2016 18:22:11 (5931 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.47137978 = "2500" 28/04/2016 18:22:11 (5955 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.47139534 = "3300" 28/04/2016 18:22:12 (5977 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.47141122 = "291" 28/04/2016 18:22:12 (6002 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.47577445 = "0" 28/04/2016 18:22:12 (6026 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.47817632 = "478" 28/04/2016 18:22:12 (6052 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.47975023 = "414" 28/04/2016 18:22:12 (6076 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.49049946 = "1" 28/04/2016 18:22:12 (6102 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.49072097 = "257" 28/04/2016 18:22:12 (6127 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.49073717 = "3328" 28/04/2016 18:22:12 (6203 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.49413261 = "11200" 28/04/2016 18:22:12 (6225 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.49540252 = "1499" 28/04/2016 18:22:12 (6248 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.49541840 = "1206" 28/04/2016 18:22:12 (6270 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.50398856 = "315" 28/04/2016 18:22:12 (6298 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.50469697 = "305" 28/04/2016 18:22:12 (6321 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.50652145 = "1202" 28/04/2016 18:22:12 (6346 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.50653701 = "1810" 28/04/2016 18:22:12 (6369 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.51058413 = "0" 28/04/2016 18:22:12 (6393 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.52735596 = "1372" 28/04/2016 18:22:12 (6470 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.53687180 = "8800" 28/04/2016 18:22:12 (6494 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.54341808 = "48" 28/04/2016 18:22:12 (6517 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.54637483 = "-32768" 28/04/2016 18:22:12 (6539 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.54767329 = "0" 28/04/2016 18:22:12 (6562 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.55094062 = "1199" 28/04/2016 18:22:12 (6589 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.55095650 = "2502" 28/04/2016 18:22:12 (6613 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.55495795 = "7080" 28/04/2016 18:22:12 (6637 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.55660835 = "323" 28/04/2016 18:22:12 (6664 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.55906083 = "6999" 28/04/2016 18:22:12 (6688 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.55976419 = "0" 28/04/2016 18:22:12 (6715 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.56104716 = "1499" 28/04/2016 18:22:12 (6741 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.56106304 = "748" 28/04/2016 18:22:12 (6769 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.56120884 = "47" 28/04/2016 18:22:12 (6792 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.56240695 = "1199" 28/04/2016 18:22:12 (6819 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.56242251 = "5002" 28/04/2016 18:22:12 (6840 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.56253481 = "890" 28/04/2016 18:22:12 (6868 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.56256689 = "1000" 28/04/2016 18:22:12 (6889 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.56258245 = "1099" 28/04/2016 18:22:12 (6914 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.56384724 = "2100" 28/04/2016 18:22:12 (6937 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.56440916 = "1000" 28/04/2016 18:22:12 (6962 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.56442600 = "5000" 28/04/2016 18:22:13 (6987 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.56588093 = "1100" 28/04/2016 18:22:13 (7012 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.56589681 = "2500" 28/04/2016 18:22:13 (7036 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.56591237 = "748" 28/04/2016 18:22:13 (7061 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.57004905 = "1000" 28/04/2016 18:22:13 (7086 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.57008113 = "1499" 28/04/2016 18:22:13 (7109 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.57009669 = "750" 28/04/2016 18:22:13 (7137 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.57221538 = "-32768" 28/04/2016 18:22:13 (7161 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.57269142 = "7080" 28/04/2016 18:22:13 (7187 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.57558313 = "1800" 28/04/2016 18:22:13 (7210 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.57559933 = "743" 28/04/2016 18:22:13 (7235 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.57857335 = "1199" 28/04/2016 18:22:13 (7259 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.57973957 = "0" 28/04/2016 18:22:13 (7283 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.57977958 = "4938" 28/04/2016 18:22:13 (7307 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.57979578 = "1193" 28/04/2016 18:22:13 (7331 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.58055936 = "999" 28/04/2016 18:22:13 (7352 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.58057556 = "1099" 28/04/2016 18:22:13 (7377 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.58059240 = "1000" 28/04/2016 18:22:13 (7398 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.58262547 = "52" 28/04/2016 18:22:13 (7426 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.59227245 = "449" 28/04/2016 18:22:13 (7449 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.61066755 = "3306" 28/04/2016 18:22:13 (7471 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.61068375 = "901" 28/04/2016 18:22:13 (7493 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.61070059 = "254" 28/04/2016 18:22:13 (7517 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.61072640 = "748" 28/04/2016 18:22:13 (7538 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.61074260 = "5000" 28/04/2016 18:22:13 (7563 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.61075944 = "1199" 28/04/2016 18:22:13 (7585 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.61178010 = "25" 28/04/2016 18:22:13 (7608 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.61220332 = "1815" 28/04/2016 18:22:13 (7631 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.61221920 = "752" 28/04/2016 18:22:13 (7658 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.61362006 = "1800" 28/04/2016 18:22:13 (7679 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.61368969 = "756" 28/04/2016 18:22:13 (7704 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.61370589 = "1003" 28/04/2016 18:22:13 (7727 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.61373861 = "1802" 28/04/2016 18:22:13 (7749 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.61526345 = "3330" 28/04/2016 18:22:13 (7770 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.61527965 = "280" 28/04/2016 18:22:13 (7793 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.61560767 = "1000" 28/04/2016 18:22:13 (7817 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.61562355 = "750" 28/04/2016 18:22:13 (7844 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.61565531 = "1099" 28/04/2016 18:22:13 (7866 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.62072951 = "302" 28/04/2016 18:22:13 (7891 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.62867599 = "276" 28/04/2016 18:22:13 (7913 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.62869187 = "3320" 28/04/2016 18:22:13 (7938 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.62930326 = "1000" 28/04/2016 18:22:13 (7961 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.62932010 = "1499" 28/04/2016 18:22:14 (7983 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.63002067 = "999" 28/04/2016 18:22:14 (8004 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.63003751 = "751" 28/04/2016 18:22:14 (8030 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.63005371 = "1499" 28/04/2016 18:22:14 (8051 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.63237143 = "912" 28/04/2016 18:22:14 (8074 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.63238827 = "3288" 28/04/2016 18:22:14 (8098 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.63433545 = "330" 28/04/2016 18:22:14 (8121 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.63915527 = "1800" 28/04/2016 18:22:14 (8144 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.63917147 = "1799" 28/04/2016 18:22:14 (8170 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.64355058 = "0" 28/04/2016 18:22:14 (8191 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.64595213 = "673" 28/04/2016 18:22:14 (8219 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.64752636 = "52" 28/04/2016 18:22:14 (8240 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.65825939 = "0" 28/04/2016 18:22:14 (8263 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.65849678 = "17" 28/04/2016 18:22:14 (8286 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.66237848 = "6990" 28/04/2016 18:22:14 (8309 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.66317929 = "1801" 28/04/2016 18:22:14 (8332 ms) : 1.3.6.1.4.1.9.9.91.1.1.1.1.4.66319549 = "1200"
----------------------- New Test ----------------------- Paessler SNMP Tester 5.1.3 28/04/2016 18:29:07 (1 ms) : Device: 103.1.134.5 28/04/2016 18:29:07 (2 ms) : SNMP V2c 28/04/2016 18:29:07 (2 ms) : Walk 1.3.6.1.2.1.47.1.1.1.1.7 28/04/2016 18:29:07 (16 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.14289 = "slot mau TenGigE0/0/CPU0/3" 28/04/2016 18:29:07 (25 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.67605 = "current 0/0/CPU0/2" 28/04/2016 18:29:07 (34 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.138542 = "temperature 0/FT1/SP" 28/04/2016 18:29:07 (44 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.320862 = "voltage 0/RSP0/CPU0" 28/04/2016 18:29:07 (54 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.322450 = "voltage 0/RSP0/CPU0" 28/04/2016 18:29:07 (64 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.727162 = "power Rx 0/1/CPU0/2" 28/04/2016 18:29:07 (76 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.2080513 = "fan5 0/FT1/SP" 28/04/2016 18:29:07 (86 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.2082133 = "fan1 0/FT1/SP" 28/04/2016 18:29:07 (100 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.2237736 = "module 0/PM1/SP" 28/04/2016 18:29:07 (110 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.2359704 = "cpu 0/RSP0/CPU0" 28/04/2016 18:29:07 (119 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.2404345 = "power Tx 0/2/CPU0/2" 28/04/2016 18:29:07 (131 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.2905431 = "module mau GigabitEthernet0/1/CPU0/4" 28/04/2016 18:29:07 (142 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.3327592 = "slot mau TenGigE0/2/CPU0/2" 28/04/2016 18:29:07 (153 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.3355929 = "voltage 0/PM0/SP" 28/04/2016 18:29:07 (165 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.3706445 = "slot mau TenGigE0/2/CPU0/1" 28/04/2016 18:29:07 (176 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.4010525 = "temperature 0/2/CPU0/7" 28/04/2016 18:29:07 (187 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.4220122 = "TenGigE0/0/0/0" 28/04/2016 18:29:07 (198 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.4306232 = "current 0/1/CPU0/0" 28/04/2016 18:29:07 (209 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.4410815 = "TenGigE0/0/0/2" 28/04/2016 18:29:07 (220 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.4412403 = "TenGigE0/0/0/6" 28/04/2016 18:29:07 (238 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.4436046 = "temperature 0/1/CPU0/19" 28/04/2016 18:29:07 (250 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.4437634 = "voltage 0/1/CPU0/19" 28/04/2016 18:29:07 (262 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.4553394 = "module mau GigabitEthernet0/1/CPU0/0" 28/04/2016 18:29:07 (274 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.4639747 = "slot mau GigabitEthernet0/1/CPU0/5" 28/04/2016 18:29:07 (287 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.4761191 = "voltage 0/1/CPU0" 28/04/2016 18:29:07 (299 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.4762811 = "voltage 0/1/CPU0" 28/04/2016 18:29:07 (310 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.5029108 = "module mau TenGigE0/0/CPU0/3" 28/04/2016 18:29:07 (322 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.5329584 = "current 0/0/CPU0/1" 28/04/2016 18:29:07 (335 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.5574832 = "voltage 0/0/CPU0" 28/04/2016 18:29:07 (351 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.5645168 = "temperature 0/1/CPU0/1" 28/04/2016 18:29:07 (363 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.5773465 = "voltage 0/0/CPU0" 28/04/2016 18:29:07 (377 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.5775149 = "voltage 0/0/CPU0" 28/04/2016 18:29:07 (389 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.5778357 = "voltage 0/0/CPU0" 28/04/2016 18:29:07 (400 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.5789569 = "temperature 0/2/CPU0/0" 28/04/2016 18:29:07 (413 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.5909380 = "voltage 0/2/CPU0" 28/04/2016 18:29:07 (427 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.5922230 = "voltage 0/0/CPU0" 28/04/2016 18:29:07 (442 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.5925406 = "voltage 0/0/CPU0" 28/04/2016 18:29:07 (455 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.5926994 = "voltage 0/0/CPU0" 28/04/2016 18:29:07 (468 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.6106457 = "voltage 0/2/CPU0" 28/04/2016 18:29:07 (484 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.6109729 = "voltage 0/2/CPU0" 28/04/2016 18:29:07 (503 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.6111349 = "voltage 0/2/CPU0" 28/04/2016 18:29:07 (520 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.6256778 = "voltage 0/2/CPU0" 28/04/2016 18:29:07 (536 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.6258398 = "voltage 0/2/CPU0" 28/04/2016 18:29:07 (551 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.6259986 = "voltage 0/2/CPU0" 28/04/2016 18:29:07 (568 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.6673654 = "voltage 0/2/CPU0" 28/04/2016 18:29:07 (584 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.6676830 = "voltage 0/2/CPU0" 28/04/2016 18:29:07 (600 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.6678418 = "voltage 0/2/CPU0" 28/04/2016 18:29:08 (619 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.6869781 = "speed 0/FT1/SP" 28/04/2016 18:29:08 (635 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.6888699 = "power Rx 0/1/CPU0/1" 28/04/2016 18:29:08 (651 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.7227062 = "voltage 0/0/CPU0" 28/04/2016 18:29:08 (667 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.7228618 = "voltage 0/0/CPU0" 28/04/2016 18:29:08 (681 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.7357110 = "fan5 0/FT0/SP" 28/04/2016 18:29:08 (696 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.7358666 = "fan1 0/FT0/SP" 28/04/2016 18:29:08 (715 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.7526020 = "voltage 0/0/CPU0" 28/04/2016 18:29:08 (733 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.7641118 = "voltage 0/1/CPU0/4" 28/04/2016 18:29:08 (748 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.7642706 = "temperature 0/1/CPU0/4" 28/04/2016 18:29:08 (766 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.7645119 = "temperature 0/1/CPU0" 28/04/2016 18:29:08 (782 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.7646707 = "voltage 0/1/CPU0" 28/04/2016 18:29:08 (800 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.7648263 = "voltage 0/1/CPU0" 28/04/2016 18:29:08 (818 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.7726369 = "voltage 0/0/CPU0" 28/04/2016 18:29:08 (840 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.7727989 = "voltage 0/0/CPU0" 28/04/2016 18:29:08 (859 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.7921950 = "module mau TenGigE0/2/CPU0/3" 28/04/2016 18:29:08 (882 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.7931360 = "power Rx 0/0/CPU0/4" 28/04/2016 18:29:08 (907 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.8695772 = "module 0/1/CPU0" 28/04/2016 18:29:08 (931 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.8784399 = "slot mau TenGigE0/0/CPU0/1" 28/04/2016 18:29:08 (954 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.8895994 = "current 0/0/CPU0/7" 28/04/2016 18:29:08 (978 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.9840949 = "module mau TenGigE0/1/CPU0/1" 28/04/2016 18:29:08 (1002 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.10030546 = "slot mau GigabitEthernet0/1/CPU0/2" 28/04/2016 18:29:08 (1023 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.10110611 = "slot 0/PM2" 28/04/2016 18:29:08 (1045 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.10154515 = "cpu 0/RSP1/CPU0" 28/04/2016 18:29:08 (1068 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.10170036 = "slot 0/3" 28/04/2016 18:29:08 (1093 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.10735504 = "voltage 0/RSP1/CPU0" 28/04/2016 18:29:08 (1117 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.10737188 = "voltage 0/RSP1/CPU0" 28/04/2016 18:29:08 (1141 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.10738808 = "temperature 0/RSP1/CPU0" 28/04/2016 18:29:08 (1165 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.10743073 = "voltage 0/2/CPU0" 28/04/2016 18:29:08 (1190 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.10744693 = "voltage 0/2/CPU0" 28/04/2016 18:29:08 (1215 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.10845139 = "temperature 0/1/CPU0/0" 28/04/2016 18:29:08 (1239 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.10889081 = "voltage 0/1/CPU0" 28/04/2016 18:29:08 (1261 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.10890637 = "voltage 0/1/CPU0" 28/04/2016 18:29:08 (1284 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.10892225 = "voltage 0/1/CPU0" 28/04/2016 18:29:08 (1312 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.11029231 = "voltage 0/2/CPU0" 28/04/2016 18:29:08 (1336 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.11037718 = "voltage 0/1/CPU0" 28/04/2016 18:29:08 (1359 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.11039402 = "voltage 0/1/CPU0" 28/04/2016 18:29:08 (1382 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.11042610 = "voltage 0/1/CPU0" 28/04/2016 18:29:08 (1404 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.11196778 = "power Tx 0/1/CPU0/18" 28/04/2016 18:29:08 (1426 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.11229452 = "voltage 0/2/CPU0" 28/04/2016 18:29:08 (1448 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.11231040 = "voltage 0/2/CPU0" 28/04/2016 18:29:08 (1467 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.11234344 = "voltage 0/2/CPU0" 28/04/2016 18:29:08 (1489 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.11239623 = "voltage 0/1/CPU0" 28/04/2016 18:29:08 (1512 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.11329318 = "slot mau GigabitEthernet0/1/CPU0/13" 28/04/2016 18:29:08 (1533 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.11741636 = "power Tx 0/0/CPU0/3" 28/04/2016 18:29:08 (1557 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.11741762 = "speed 0/FT1/SP" 28/04/2016 18:29:08 (1577 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.12536348 = "power Tx 0/1/CPU0/3" 28/04/2016 18:29:08 (1599 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.12597551 = "voltage 0/2/CPU0" 28/04/2016 18:29:09 (1620 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.12599139 = "temperature 0/2/CPU0" 28/04/2016 18:29:09 (1642 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.12602315 = "voltage 0/2/CPU0" 28/04/2016 18:29:09 (1664 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.12670880 = "voltage 0/0/CPU0" 28/04/2016 18:29:09 (1684 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.12672500 = "voltage 0/0/CPU0" 28/04/2016 18:29:09 (1707 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.12674056 = "voltage 0/0/CPU0" 28/04/2016 18:29:09 (1726 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.12905956 = "voltage 0/RSP0/CPU0" 28/04/2016 18:29:09 (1751 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.12907576 = "voltage 0/RSP0/CPU0" 28/04/2016 18:29:09 (1773 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.13102294 = "power Tx 0/2/CPU0/3" 28/04/2016 18:29:09 (1794 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.13222512 = "slot mau GigabitEthernet0/1/CPU0/19" 28/04/2016 18:29:09 (1813 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.13443524 = "speed 0/FT1/SP" 28/04/2016 18:29:09 (1835 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.13584276 = "voltage 0/0/CPU0" 28/04/2016 18:29:09 (1855 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.13585960 = "voltage 0/0/CPU0" 28/04/2016 18:29:09 (1873 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.13805629 = "speed 0/FT0/SP" 28/04/2016 18:29:09 (1891 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.14020599 = "voltage 0/1/CPU0/7" 28/04/2016 18:29:09 (1910 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.14022155 = "temperature 0/1/CPU0/7" 28/04/2016 18:29:09 (1932 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.14031228 = "slot mau GigabitEthernet0/1/CPU0/15" 28/04/2016 18:29:09 (1951 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.14263962 = "current 0/0/CPU0/0" 28/04/2016 18:29:09 (1970 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.14421321 = "temperature 0/0/CPU0/5" 28/04/2016 18:29:09 (1988 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.14578394 = "TenGigE0/1/0/0" 28/04/2016 18:29:09 (2006 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.14924172 = "GigabitEthernet0/1/0/18" 28/04/2016 18:29:09 (2024 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.14925760 = "GigabitEthernet0/1/0/14" 28/04/2016 18:29:09 (2045 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.15076145 = "GigabitEthernet0/1/0/4" 28/04/2016 18:29:09 (2063 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.15077701 = "GigabitEthernet0/1/0/8" 28/04/2016 18:29:09 (2082 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.15117093 = "slot mau GigabitEthernet0/1/CPU0/7" 28/04/2016 18:29:09 (2101 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.15177601 = "speed 0/FT0/SP" 28/04/2016 18:29:09 (2120 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.15363571 = "TenGigE0/2/0/4" 28/04/2016 18:29:09 (2142 ms) : 1.3.6.1.2.1.47.1.1.1.1.7.15400432 = "MgmtEth0/RSP1/CPU0/1" 28/
Created on May 6, 2016 4:26:13 AM
Last change on May 6, 2016 5:42:35 AM by
Luciano Lingnau [Paessler]
Votes:
The results from the SNMP Tester look fine, if the Tester can read the values PRTG can as well, ensure that:
Alternatively, please consider that you should be able to use the SNMP Custom Table Sensor on the entSensorValueTable (1.3.6.1.4.1.9.9.91.1.1.1) and use [1.3.6.1.2.1.47.1.1.1.1.7] as part of the Sensor's Name that way the sensor will display the correct name automatically. Please be aware that tis sensor doesn't support native "scale adjustment" in the sensor's settings (in the same fashion as the SNMP Custom sensor does) but you could set the Scaling Multiplication and Scaling Division within the channel settings for similar results.
Best Regards,
©2025 Paessler AG Terms & Conditions Privacy Policy Legal Notice Download & Install
Add comment