This is no solution for environmental values.
The native Rittal CMC-III Sensor in PRTG offers Hardware-Status Monitoring with lookups, that's ok but not the only scope here.
In short (long way was 4 working-days):
I got it working by first using the snmp custom table sensor to walk through the OID table (1.3.6.1.4.1.2606.7.4.2.2) with the environmental values coloumns (1.3.6.1.4.1.2606.7.4.2.2.1.11) to get the complete OID per value and if needed, the enum / scope parameters if you (I did) want to use lookup-tables.
Then I used the snmp custom advanced sensor to build sensors with channels, e.g. sensor = temperatures, channels = server-in,server-out, water-in,water-out, etc...
After this, i added based on the lookup "oid.rittal-cmc-iii-mib.cmciiimsg.cmciiimsgstatus.ovl" my own lookups for status of LCP-valve, LCP-fans, Leakage-Sensor and then I added some more snmp custom advanced sensors for this. you can contact me if you need some files / examples.