APC UPS threshold notify setting

Votes:

0

I have APC UPS to monitor with PRTG. It has PowerNet-MIB ups adv battery sensor. I 'd like to send notification when its battery below 50 % or 30 minute remaining. How can I set that threshold notification? I saw " When PowerNet-MIB ups adv battery sensor" Channel is below " XXX " for at least 60 minute.

I don't know what xxx mean. its is minute or second or hour? Then I can set it correctly.

Regards.,

apc snmp ups

Created on Jul 3, 2021 9:15:33 AM



1 Reply

Votes:

0

Hello,

Thank you for your message.

The value defined in the threshold trigger will be compared to the one from the channel defined. Here is the manual of the threshold trigger: https://www.paessler.com/manuals/prtg/sensor_notifications_settings#threshold

For example, let's take a channel called Battery left, which return the percentage of remaining battery. Then, the value configured for the trigger will check if that percentage is below 50% and trigger the corresponding notification template:


When Battery left (%) is below 50 for at least 30 seconds, perform notification


If you have questions, let us know.

Regards.

Created on Jul 5, 2021 10:07:22 AM by  Florian Lesage [Paessler Support]